I have always wondered as to why does a circuit breaker in the IEC World have so many
short circuit breaking capacities such as Ics(service short circuit breaking capacity),
Icu(ultimate short circuit breaking cap), Icw (short circuit breaking capacity). After running
an ETAP Programme we reach an initial symmetrical short circuit current (say 40 kA) which
in turn determine the short circuit rating of the switchgear for 1sec/3 sec( I..E 40kA for 1
second). Some of the suppliers consider it as the prospective short circuit current and match
the Icu rating of the breaker( 40kA) to be used on such a switchgear . Shouldn't they select
Icw rating of the breaker to match the switchgear short circuit withstand current for 1 sec.
Your suggestions will be of great help.

dede61 (Electrical)11 Dec 03 07:29


Hi Uno,
Breaking capacity of the CB must always exceed the short circuit withstand current of the
switchgear. So the requirement of the switchgear will determinate the Short circuit breaking
capacity of your CB. Standard (depending the application) the Icw rating of the breaker
should exceed the switchgear rating.
regards,
Danny
4

davrom (Electrical)11 Dec 03 12:44


Please excusse my English. Can you re-phrase the sentence "which in turn determine the
short-circuit rating of the switchgear for 1sec/3sec (i.e. 40kA for 1 second)"? I don't
understand. Thank you.
For Icw (selection of CB based on the shc current value at time 1 second): No. The breaking
capacity/current Icw of CB is to be based on the value of short-circuit current calculated at
the time when the CB's contacts start to separate, which in most cases is abt. tens of msec
not 1 second; this time is to be obtained from CB data sheet.
For the rest of currents, please give 1-2 days.
(I would suggest you to visit the question "system stability" of this Forum).

uno (Electrical)
(OP)

12 Dec 03 03:45
Thanks Danny and Davrom for your responses.
Davrom
The 1 second or 3 second is to specify the short time withstand rating of the fault current
during which the prospective fault current(I..E 40kA) is assumed to be constant.
I agree with Danny in that the breaking capacity of the breaker should be Icw and should
match the switchear short circuit withstand level. On some more investigation I also found
that some breakers ( in utilization category A) need not have Icw rating since they do not
have intentional time delay under short circuit condition. Then how do we confirm that the
breaker selected by the supplier is ok?

davrom (Electrical)14 Dec 03 07:03

Hi uno.
A. Please forget my first message.
B. Sorry for this delayed response. My attempt to understand the differences between the
three currents took me more than 1-2 days that I expected. I have been checking for and
thinking to the three currents over and over again. I have come to some conclusions, but, as
I am not 100% sure, I recommend you to take my below notes as suggestion only.
1. The name of Icw is "rated short-time withstand current" and has nothing to do with
breaking capacity (this confused me). The physical meaning of Icw is more close to the
making current Icm than to breaking current(s).
2. The making current Icm must be biger than the peak value ip of shc current and specifies
the maximum curent which the CB withstand to in respect to the electro-dynamic forces
produced by the inrush current of shc.
3. For CBs with intentionally time delay and resp. with Icw, the CB must be able to withstand
to the shc current (el-dynamic forces) for the duration of the set delay (e.g. 100 msec) and
then to break/trip the circuit (Icu) if the shc is still present. This is why I afirm that the Icw is
more close in meaning to the Icm. The Icw is to be bigger than r.m.s. value of iksym
assumed to be constant from the begining of shc (i.e. 40 kA for 1/3 seconds in your case).
4. Utilization category A means that the CB is not intended to be used in series with another
protection device in supply line; this would be coresp. to the motor protection CBs of
Siemens.
5. Utilization category B means that the CB is intended to be used in series with another
protective device in supply line; this would be coresp. to the line protection CBs of Siemens.
Consequently, in order to ensure the selectivity of protection, the CB is to be provided with
and intentionally delay release time (which can be adjusted) and, hence, with the Icw.
6. Based on notes 2 and 3 it results that the Icw is only defined/specified for CBs used in
category B.
7. The difference between Icu (ultimate) and Ics (service) currents consists in the qualitative
and quantitative conditions established for testing the CBs. I cannot tell exactly what is this
diference.
8. The CBs are constructed in four cases, depending of relationships between the three
currents (equal, >, <, <>), i.e. Ics=Icw<>Ics, Ics=Icw=Icu etc.
9. I have checked the Siemens products catalogue and I haven't found specified the Icw
value. I assume that all Siemens CBs are constructed with Ics=Icw. On the other hand, the
Siemens offers CBs provided to "azn" electronic device; some CBs are only with "an" device coresp. to motor protection while others are provided with "azn" device. The Icw and its
delay time can be adjusted on "z" portion of tripping characteristic, resp. from Icw=0...8*In
of CB and td=0...300 msec; t=0 msec coresp. to motor protection CB; t>0 sec coresp. to line
protection CB (categ. B); the CB can be used for both categories.
10. The Siemens states that back-up fuses are only required if the shc current at the point of
installation exceeds the Icu (ultimate) value of CB. Cumulated with the fact that Ics is in
almost cases smaller or equal with Icu, it result that the base for selection the breaking
capacity of CB is the Icu, but as I said above, I cannot tell for sure what is the difference
between Ics and Icu. A manufacturing engineer may tell this difference; I am only an

installation engineer.
11. The breaking capacity/curent of CB (Icu or Ics) is to be bigger that the shc current
evaluated at the time when the CB's contacts start to separate. This value is to be based on
the r.m.s. value of the iksym at the time when the contacts start to separate; I personally
prefer to calculate the instantaneous value of shc current (ikasym+iksym) at the respective
moment.
12. As far as I am concerned, I "split" the short-circuit process into three sequences:
a) t=0...topening: the CB must be able to withstand to the el-dynamic forces produced by
the inrush current of shc; therefore, Icm > ip (please read the ">" sign as "must be bigger
than"); for CB of category B this additional condition must be met: Icw > iksym(t=0) - acc. to
note 3.
b) t=topening: the CB must be able to break/trip the shc current at this time; therefore, Icu
> Ik(r.m.s. of iksym, t=0 (assumed constant)) or, in my theory, Icu > ik(t=topening).
c) t=0...tend: the CB must be able to withstand to the heat effects produced by the shc
current in the interval t=0...topening and by electric arc between opened contacts in the
interval t=topening...tend; therefore, Ilt > Ith (thermal current).
I hope my notes would be of a help to you, but as I said before, I recommend you take this
scheme as suggestion only.

davrom (Electrical)14 Dec 03 07:06


Correction to my previous message:
At note 6 please read "based on notes 4 and 5 ...".

uno (Electrical)
(OP)

15 Dec 03 03:20
Thanks a ton Davrom
A star to your post. I don't know how I reached the conclusion that Icw is the breaking
capacity. I guess then the manufacturer's do the right thing in considering Icu for the
selection of breakers for a switchgear.
Meanwhile I also checked The IEC 947-2 and reached the following conclusion When the breaker is tested for Icu , after which it cannot be expected to carry the rated
current continuosly which is not the case when tested for Ics.
Thanks a lot for all your responses.
2

Area (Electrical)15 Dec 03 05:27


Uno,
sorry for the late reply, but I saw your post just today. It has allready been perfectly tackled
by davrom, theefore just my understanding as additional information as I had the same
problem in the past:
the result of your ETAP program should be:
- Ik": Initial short circuit current (rms value): Maximum value of the 3 pole short circuit
current. Occurs directly after the initiation: Network feeders, generators and motors
contribute to this value
- ip: Peak short circuit current (peak value, not rms value). Maximum value (peak value) of
the short circuit current. Occurs within the first sin half wave directly after the initiation.
furthermore, you can also obtain these values from such programs, that are both derived
from Ik":

- Ik: Steady state short current (short circuit current after the decaying of the d.c.
component). Derived from Ik". Only network feeders and generators contribute to this value
- Ib: Symmetrical short circuit breaking current: rms value of the short circuit at the moment
when the breaker opens. Derived from Ik". The influence of motors and gnerator is reduced
compared to Ik"
Generally speaking, Ik", Ik and Ib are referring to the thermal stress of your equipment, while
ip is referring to the mechanical stress of your equipment.
You do not need Ik and Ib in any case. You can use Ik" instead to be on the safe side.
Rated values of a SCB:
- ICM: (peak value): Max value that the SCB can carry. The greatest stress to be managed is
during closing on a short circuit current. There, the mechanical stress has to be managed.
- ICU: (rms-value): Max current that the short circuit breaker can break without beeing in a
dangerous condition afterwards
- ICS: (rms-value): Same as ICU. The difference is, that the SCB might be defective after the
operation. Therefore, this value is often expressed in % of ICU (0..100%). The higher this
value is, the better is the quality of the SCB.
- ICW: (rms value): The maximum value that the SCB can carry (without breaking) of a
specified time (very often 1sec. or 3sec.)
For the correct choice of your short circuit breaker applies:
Mech. stress: ICM > ip
Thermal stress: ICU >= ICS > Ib and ICW > Ik"
or instead of this : ICU >= ICS >= ICW > Ik"

Voo (Electrical)16 Dec 03 05:03


As far as I know, the BS EN 60947-2 (derivative of IEC 947-2) only defines the following
standard terminology concerning the current rating for MCCB/ACB:
In Rated current
The maximum continuous current a CB will carry under healthy circuit conditions. I shall not
elaborate it further.
Icu Rated ultimate short circuit (sc) breaking capacity
The maximum prospective fault current level a CB can withstand.
Ics Rated service sc breaking capacity
The maximum level of fault current operation the CB will withstand and still remain in full
performance after the fault.
Icw Rated short time withstand current
The current the CB can withstand for the maximum short time delay time.
I do not know whether , Icm, the so-called making capacity of CB is defined in any IEC
standard. But I did find Icm rating in a CB manufacturer catalogue. From what I know the
term prospective fault current level in the IEC standard always refer to symmetrical steady
state fault level and the IEC 947-2 does not define any standard test for asymmetrical fault
current rating for CB. As such I do not know on what basis of method each CB manufacturer
defines the Icm rating

Actually the differences of Icu and Ics rating lies between the method the CB is tested in
accordance to the IEC standard.
Icu The CB under test must subjected to a test sequences of O-CO with no performance
loss at the end of test.
Ics The CB under test must subjected to test sequences of O-CO-CO with no performance
loss at the end of test.
Where
O
Opening operation under fault conditions.
C- Closing operation on to a fault.
As can be seen from above, CB under Ics test undergoes more steps. Therefore the we could
always expect the fault level a CB can achieve under the Ics test condition to be equal or
lower than the fault level it can go through under the Icu test condition. Ics is usually
indicated as a percentage of Icu (say 100%, 75%, 50% etc.)
Icu capacity indicates the maximum theoretical fault level of the CB and this has to be
matched (equal or higher) with the calculated prospective fault (symmetrical) value of the
installation at the point of connection (i.e. the switchboard kA rating).
For example a CB of Icu = 50kA and Ics = 50% Icu means that that CB can withstand
maximum fault up to 50kA and up to 25kA fault for continuation of service. In other words, if
fault levels are between 25kA to 50kA, the CB still able to cut out the faulty circuit safely but
its further operation afterward is not assured. If the fault level is 25kA and below then the CB
is able to cut out the faulty circuit safely and its further operation afterward is assured.
It can be seen that Ics applies to short circuit faults that could occur in practice. In my
country, the specification usually called for Ics be 100% of Icu for incoming feeder and 50%
of Icu for outgoing feeder.
I have never specify the value for Icm (neither does I know what IEC definition for it). It is my
opinion that Icm shall only be taken into account in special installation which consist
majority of heavy motors, generators etc. Perhaps <Area> can elaborate the definition of
thermal stress and mechanical stress of the CB as well as Icm with relevance to any IEC
standard or equivalent.
As for the Icw it is more to coordination curve of CB for downstream consideration and bear
no relevance to Ics or Icu.

davrom (Electrical)16 Dec 03 07:52


To Voo:
1. A star to your post. Real thanks for info given upon the Icu and Ics currents. I knew the
test sequences of each current (qualitative conditions) and the capability of CB to carry,
resp. not to carry its rated current (quantitative conditions), but I couldn't understood the
physical meaning of these conditions. Now all is clear. Thanks again.
2. The definition of making current Icm can be found in the IEC 60977-1 "LV Switchgear and
Controlgear. Part 1: General rules" and IEC 60977-2 "LV Switchgear and Controlgear. Part 2:
Circuit breakers".
The making current Icm is reffered as the peak value ip (instantaneous value, in kA) of the
short-circuit current to which the CB withstand, in respect to the electro-dynamic forces (or
"mechanical stress" - area).

I believe that area's terms "mechanical stress" resp. "thermal stress" are the same with my
terms "dynamic stability" resp. "thermal stability" and reffer to the physical phenomena
occured during a short-circuit.
A current which flows through a conductor or a current path (e.g. CB's contacts) produces an
electro-magnetical field around the conductor. The physical expression of this field is the
force which the conductor interracts with the elements in its vecinity. The force value is
directly proportional with value of current.
Also, the same current causes the conductor to get heated; the heat is being transfered to
the medium in which the conductor is placed and determine the temperature to rise in the
respective medium/space; this has impact on the dielectric properties of the estinguishing
medium (the a.m. IEC Part2 specifies a dielectric test to be performed for CBs). The
temperature rise is directly proportional with the value of current.
The short-circuit current produces an inrush force on the CB's contacts and determine a
rapidly increase of the temperature in medium/space of contacts. The maximum
instantaneous value of the force is reached for the peak value of the short-circuit current.
Based on this, the making current Icm indicates in fact the maximum force to which the CB
withstand (and keep its contacts closed).
In order to make easier the selection of a CB based on the short-circuit current value
(expressed in kA), it has been choosen to indicate the values of the currents that produce
the repective force resp. temperature rise, instead to be given the values of force and
temperature to which the CB withstand.
I hope you will understand something from my notes. I am sorry, but I cannot explain better.

Area (Electrical)19 Dec 03 03:13


Davrom,
thanks for giving the link to the IEC concerning the definition of Icm. I also appreciate your
description of the Icm - could not do it better. Maybe it was not fully clear to what I was
referring with mechanical stress and thermal stress, but it is exactly what you wrote:
Mechanical stress = dynamic stability
Thermal stress = thermal stability
As you described, during a short circuit you have two phenomenoms: A 'mechanical force'
that is caused by the current and that is directly proportional to the value of the current and
a thermal loss (I^2*t), that is depending on the value of the current and on the duration
time of the short circuit. If you have e.g. a big short circuit current fort a short time (e.g. 20
msec), you will have a big mechanical stress of your equipment (SCB, switchgear) but a
minor thermal stress, as the duration time is limited. If you have a big short circuit for a
long time (let's say 300 msec), you have both problems: A big mechanical stress at the
inition of the short circuit and a big thermal stress during the short circuit.
Voo, if you did not find the Icm rating in any manufacturers catalogue, you might want to try
this link (hope it works):
http://138.227.174.121/GLOBAL/SCOT/SCOT209.nsf/VerityDi...
$File/Emax_Overview.pdf
If it does not work, access the ABB website and search for the description of the Emax series
for example.
In fact you are right not to look at the Icm value, as it is usually directly linked to the Icu
value of the short circuit breaker (e.g. the ratio for the Emax series is 2,2, meaning a SCB
rated Icu 65kA is rated Icm 143kA), as the ip value in your short circuit calculation is directly
linked to the Ik" value. Therefore, it is usually sufficient to make sure that Icu > Ik".
However, I prefer to check the Icu rating to be on the safe side.

jbartos (Electrical)20 Dec 03 16:12

Suggestions:
1. The various current limit definitions are not including the current waveform classification,
e.g. root-mean-square (rms) value, peak, symmetrical rms, asymmetrical rms, asymmetrical
peak, etc.
2. Low voltage circuit breakers have different operating duties then medium and high
voltage circuit breaker. Therefore, not all current limits are posted by the manufacturer, and
some of them may coincide.
3. Visit
http://www.schneider-electric.com.gr/pdf/Technical_Libr...
for and example of current limits included on rating plate, on page 2.
4. Low voltage circuit breakers, medium voltage circuit breakers, etc. are normally covered
by their own industry standards, respectively.