A Control Design reader writes: I'm adding a conveyor section to the end of an outfeed conveyor that
changes speed due to production demand, and I plan to install a variable frequency drive (VFD). With some
products, both conveyors must match speed. What are my options for synchronizing the speed of the new
downstream conveyor to the existing conveyor?

Also, depending on the product run, the downstream conveyor will need to run faster to singulate the product,
and the distance between product will need to be programmable (+/-0.75 in). What do you recommend? Join
the discussion in the comments section below.

Also read: Drives integrate, gain intelligence

Hide Comments

Join the discussion


We welcome your thoughtful comments.
All comments will display your user name.

1 of 7 04/09/2016 6:15
How do I synchronize conveyor speeds? https://www.controldesign.com/articles/2015/how-do-i-synchronize-co...

Comments

Upload image

Comments
Submitted by Greg Semrow on Tue, 11/10/2015 - 18:03
There are a few different ways to synchronize the speed of the two conveyors. The easiest might be to
pass the speed reference from the VFD on the out feed conveyor to the VFD on the new downstream
conveyor. If the downstream conveyor needs to be operated at a different speed (faster) most VFD's
have a trim scale that would allow you to program +/-% of line speed. If the gap between products needs
to be precious and programmable you will most likely require a PLC, and other control products. Greg
Semrow - Product Line Manager - ABB Low Voltage Drives

Reply
Submitted by Scott Cunningham on Wed, 11/11/2015 - 10:31
First - you will need to decide if you need similar speed or synchronized speed. Similar speed is akin to
setting two VFDs at 60 Hz - they should be running at the same speed, but they will be a few RPM off due
to slip. Synchronized speed is where the second conveyor turns 10 degrees when the first conveyor turns
10 degrees (electronic line shaft). If you need synchronized speed (either 1:1 or 1:1.23), you will need an
encoder on the outfeed conveyor and a closed loop drive that supports electronic gearing with adjustable
ratio for you different product requirements. You will need to supply a product signal to the drive to choose
the desired ratio. If you need similar speed, you will need a basic VFD that supports different presets and
use the same command signaling the outfeed VFD uses. You will need to supply a product signal to the
drive to choose the desired ratio (same speed, 3% faster, etc). If possible, alter your machine PLC to
incorporate the signaling of your conveyor so the user only needs to go to one location to change the
product.

Reply
Submitted by John Uzzolino on Tue, 11/24/2015 - 14:49
There are a couple ways this can be accomplished, but the common principle is that there needs to be a
signal that relates the speed of the existing outfeed conveyor to the VFD on the new conveyor. First, I will
assume that the existing outfeed conveyor already has a VFD installed since the reader says it is already
variable speed based on production. Next, you will need a signal to reference the speed of the new
conveyor. If there is an available analog output signal from the existing VFD that can be used to reference
its speed, then that signal can be used as the reference speed input into the new VFD. Another option
would be to install an encoder on the existing conveyor, which can be used as an input speed reference
to the new VFD. The first option would typically be less expense, while the second option could be easier
since you would not need to interface to the existing conveyor control system. A distributor can typically
provide you with all of the components you will need (VFD, Encoder, enclosure, safety, etc) and can
ensure you the components will work well together, provide the correct performance requirements and are
sized properly for the motor on the new conveyor. John Uzzolino Business Development Manager,
Mechatronic Solutions Lenze Americas

Reply
Submitted by Julie Eleftheriou on Tue, 12/15/2015 - 14:25
Answer provided by: Hurley Gill, Senior Applications/System Engineer at Kollmorgen The required
distance between product on the downstream conveyor would most likely be best accomplished with PM

2 of 7 04/09/2016 6:15
How do I synchronize conveyor speeds? https://www.controldesign.com/articles/2015/how-do-i-synchronize-co...

servomotor technology for its programmable acceleration and deceleration capability. A typical VFD
controller will control velocity (open or closed loop); but positon-loop closure with this technology is much
less common. PM servo controllers are commonly used to close a velocity and position loop with other
available features such as electronic gearing. Product displacement is achieved as the first or next
downstream conveyor picks up the individual product from the out-feed of the previous, while accelerating
said conveyor and thus the individual product, faster than the products production speed. Depending on
things like the product size, mass, coefficient-of-friction of the product to the conveyor belt, and required
displacement, a second downstream conveyor maybe required. For explanation we will assume two servo
controlled downstream conveyors are needed to properly separate the product. First, I would recommend
mounting a 4096_LPR Master quadrature encoder for 16,384_CPR (minimum) to the machines out-feed
(upstream conveyor or equivalent). Why not a lower resolution? Because the displacement repeatability
of the downstream servo controlled conveyor(s) is affected by the resolution of the out-feed conveyors
Master encoder (+/-). Remember, the downstream programmable servo-drive/controller cannot perform
better than its Master input. In general, if the product on the machine out-feed is back-to-back there is no
need for photo-eyes to measure distance between the individual products (e.g. out-feed could be a
product magazine or conveyor, etc.). The consistency of back-to-back product running at a given product
velocity accurately measured by the Master encoder can allow the first downstream conveyors
programmable servo-drive/controller with predetermined programmed algorithms, to appropriately
accelerate and decelerate its conveyor for a given displacement between individual products. In the
event, one or more of the product types to be separated cannot meet or cannot consistently meet the
required separation displacement/tolerance specification, a second downstream servo controlled
conveyor can be added to fine tune the displacement between individual products before packaging. In
this case photo-eyes over the first downstream conveyor can be used to measure present distance
between individual products. The second downstream conveyors programmable servo-drive/controller
would determine the present distance (from time and speed) between the individual products from its
inputs and adjust the acceleration and deceleration of its conveyor by predetermined programmed
algorithms. More photo-eyes over the second downstream conveyor could be utilized to determine actual
displacement before packaging and/or feedback to the downstream conveyors programmable servo-
drive/controller for dynamic adjustments of a displacement between given product types.

Reply
Submitted by Julie Eleftheriou on Wed, 12/16/2015 - 11:37
Answer provide by: Tim Park, Regional Applications Engineer - Eastern Zone, Danfoss Drives Americas
With the range of adjustment synchronization outlined in the question, it would appear this is a somewhat
precise synchronization requirement, but a lot of information is not provided. Id use an encoder on the
existing conveyor segment to get a line speed reference for the conveyor segment were adding. There
may be one there that we can reasonably tap into, but a new one may need to be added. Likely, the best
place to add this encoder would be on the driven motor itself. Id utilize another encoder on the shaft of
the motor on the new conveyor segment to assure optimum speed regulation. The Danfoss drive itself can
be used to alter the ratio of speeds required as the product changes. Typical Danfoss solution would
include either the VLT FL300 series or the VACON NXP series. Both would require optional encoder
interface cards to complete the package.

Reply
Submitted by Beatrice Zvosec on Wed, 12/16/2015 - 16:29
Users can more easily synchronize VFDs from Rockwell Automation with their integrated motion
capabilities and Logix-based embedded instructions. Through integrated motion, users can easily create
master/slave relationships, and a few instructions can accommodate this from simple electronic gearing
to complex electronic camming. These relationships can be turned on or off programmatically, and the
ratios can be changed quickly and easily all within ladder logic. The Allen-Bradley PowerFlex 527 and
PowerFlex 755 drives from Rockwell Automation would work well in this case. The deciding point would be
on preferences for features like power range and feedback support. For example, in this application, we
can create motor synchronization with a simple Motion Axis Gear instruction where we set the slave axis
to gear to the master at a ratio of 1. We would simply change the ratio value in this instruction to modify
our system and execute corrective moves using Motion Axis Move commands to move the conveyor
either forward or backward to create the desired spacing. Response from Franklin Ruffin, commercial
engineer for drives and motion, Rockwell Automation

3 of 7 04/09/2016 6:15
How do I synchronize conveyor speeds? https://www.controldesign.com/articles/2015/how-do-i-synchronize-co...

Reply
Submitted by Adam Bainbridge on Wed, 12/16/2015 - 21:54
The main question to ask is how accurate of control is needed. To get as little error as possible an
encoder would be placed on the feed conveyor and this would be used as a speed reference for the
conveyor. Ideally there would also be an encoder on this conveyor as well so that it can be operated in
closed loop speed control. A trim function would be used to alter the speed slightly. If a high level of
accuracy is not needed then an analog output from the feed conveyor can be used as a speed reference
for this conveyor, and we can run the conveyor an open loop speed control or sensor less vector mode.
To use these two conveyors to set gap between items on the conveyor a PLC would typically be required
and would need to measure gap and adjust the speed of the second conveyor to achieve the desired gap.
Adam Bainbridge Eaton

Reply
Submitted by Leslie Swiantek on Thu, 12/17/2015 - 12:43
Answer provided by Eaton: From: Adam Bainbridge, Technical Analyst, Variable Frequency Drives, Eaton,
Watertown, WI The main question to ask is how accurate of control is needed. To get as little error as
possible an encoder would be placed on the feed conveyor and this would be used as a speed reference
for the conveyor. Ideally there would also be an encoder on this conveyor so that it can be operated in
closed loop speed control. If a high level of accuracy is not needed then an analog output from the feed
conveyor can be used as a speed reference for this conveyor, and we can run the conveyor an open loop
speed control or sensor less vector mode. To use these two conveyors to set gap between items on the
conveyor a PLC would typically be required and would need to measure gap and adjust the speed of the
second conveyor to achieve the desired gap. From: Ben Haberkorn, Senior Engineer, Variable Frequency
Drives, Eaton, Menomonee Falls, WI Tighter accuracy would require encoder on both drives. Not so high
of accuracy analog signals can be used but there will be some amount of slip introduced in each motor
drive combination that will cause some slight variance in speeds. When trying to do gapping this would
typically require a an encoder for accurate gap spacings along with a PLC with known belt lengths and
variables entered for the required gapping.

Reply
Submitted by Leslie Swiantek on Thu, 12/17/2015 - 12:45
Answer provided by Eaton: Ben Haberkorn, Senior Engineer, Variable Frequency Drives, Eaton,
Menomonee Falls, WI Tighter accuracy would require encoder on both drives. Not so high of accuracy
analog signals can be used but there will be some amount of slip introduced in each motor drive
combination that will cause some slight variance in speeds. When trying to do gapping this would typically
require a an encoder for accurate gap spacings along with a PLC with known belt lengths and variables
entered for the required gapping.

Reply
Submitted by Julie Eleftheriou on Sat, 12/19/2015 - 21:56
Answer provided by Dan Nigro, Group Marketing Manager - Product Marketing, Omron Automation and
Safety The level of synchronization needs to be determined to understand the integration that is needed.
If synchronization means that the first and second conveyor need to follow each other in speed by a few
revolutions per minute (RPM), then sending a speed command to each drive independently will probably
be good enough. Some drives have the capability to talk to each other, meaning you could give the
command to the first drive only and the drive will communicate this speed to other drives. This simplifies
logic. Parameters could then be set to adjust a deviation speed from this commanded speed, to allow
gaps between products. If synchronization means a more precise speed following, less than a 1%
deviation, then a drive that can do full closed loop vector control will probably be needed. An encoder will
need to be mounted to the first and second conveyor so that the exact speed can be measured and
adjusted within the drive control algorithm.

Reply
Submitted by Rishi AH on Tue, 06/07/2016 - 10:59
Using an encoder in conjunction with a Master-Slave VSD configuration

4 of 7 04/09/2016 6:15
How do I synchronize conveyor speeds? https://www.controldesign.com/articles/2015/how-do-i-synchronize-co...

Reply

RSS feed for comments on this page | RSS feed for all comments

Related Content

How to select a variable frequency drive


Many drive choices are available from a variety of vendors, so some of the basics and best

How to size a motor


Calculations, advice and formulas for ensuring you have the right motor for your application.

Encoders and resolversgiving you a sense of where things are


Whether it is rotational angle, speed feedback or actuator position, rotary encoders and

Danfoss Drives trumpets the future in New Orleans


With the 2015 acquisition of Vacon, Danfoss Drives became a formidable global drives supplier

Motion Control Joins the Eciency Revolution


Smart machine builders are using innovative designs, components, software and production

Electronic controls synchronize motion for Hagerty Steel & Aluminum


Tuning three motor drives to move in a desired fashion independently of each other in

Choose Drives for Speed, Accuracy


Servo Motors and Drives Provide Advantages in Appropriate Applications

How to conserve energy and reduce noise with VFD cabling


Matching the proper cable to your VFD installation ensures reliable operation for the long

Most Popular
Past 7 Days Past 30 Days Past 6 Months All Time

01 Cybersecurity means protecting assets from remote-access threats


It is obvious that IIoT is going to create a bastion of security issues

02 NI announces CEO transition plan; board appoints new president


Alex Davern will succeed Dr. James Truchard, who has served as the CEO of

5 of 7 04/09/2016 6:15
How do I synchronize conveyor speeds? https://www.controldesign.com/articles/2015/how-do-i-synchronize-co...

03 SCADA Systems: The heart and brain of industrial automation


Digitalization of information and increasingly pervasive internet

04 The IoT starts with common and proper things


Trillions of things are getting lost in the Internet of things (IoT), big

05 Motion Industries to acquire OBBCO Safety & Supply


OBBCO Safety & Supply is an industrial safety distributor.

About
Contact Us
Advertise
Media Kit
Rates & Spec
Privacy Policy
Legal / T&C

Content
Voices
Blogs
News
White Papers
Multimedia
Special Reports
Events
Products
Technology Roundups
E-lits
Vendor News

Magazine
Subscribe
Digital Edition
Issue Archive
Reprints

Site Tools
Knowledge Center
Company Profiles

6 of 7 04/09/2016 6:15
How do I synchronize conveyor speeds? https://www.controldesign.com/articles/2015/how-do-i-synchronize-co...

Site Map

Stay Connected
My Account
Newsletters
RSS
Twitter
Facebook
Google+
LinkedIn
YouTube

Contact Us | Advertise | Privacy Policy | Legal Disclaimers, Terms & Conditions


Copyright 2004 - 2016 Control Design. All rights reserved.
P: 630-467-1300 | 1501 E. Woodfield Road, Suite 400N, Schaumburg, IL 60173

Chemical Processing | Control | Control Design | Food Processing | Pharmaceutical Manufacturing | Plant Services | Smart
Industry

7 of 7 04/09/2016 6:15

S-ar putea să vă placă și